NM cable enters a single-gang nonmetallic box that has no cable clamps. Within what distance of the box must the cable be secured?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6026
- B: 8 in
Explanation
For single-gang nonmetallic boxes not larger than 2 1/4 in by 4 in mounted in walls or ceilings, clamps are not required if the cable is fastened within 8 in of the box and the sheath extends at least 1/4 in inside. See 314.17.