A ground ring encircling a building must consist of at least 20 ft of bare copper conductor not smaller than

Exactly one answer is correct.

Show solution

Correct answer to question 5007

  • C: 2 AWG

Explanation

A ground ring must be in direct contact with the earth, encircle the building, and consist of at least 20 ft of bare copper not smaller than 2 AWG. See 250.52(A)(4).