Under the 2023 NEC, a receptacle installed to serve a dwelling kitchen island countertop must be located where?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4066
- A: On or above the countertop, or in it using a listed assembly
Explanation
The 2023 edition removed the option of mounting countertop receptacles below the countertop. Receptacles serving an island must be on or above it, not more than 20 in. above, or in the countertop using a receptacle outlet assembly listed for that use.