Question 4048 of 1003 · California General Electrician Exam
A dwelling unit fire alarm system is supplied by an individual branch circuit run in metal raceway in accordance with Article 760. Is AFCI protection required for this circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4048
- D: No, an exception permits omitting AFCI for this circuit
Explanation
AFCI protection is not required for an individual branch circuit that supplies a fire alarm system when it is run in a metal raceway, metal-clad cable or a similar wiring method as described in Article 760 (see 760.41(B) and 760.121(B)). In the 2026 edition this appears as Exception No. 1 to 210.12(B). The exception avoids nuisance tripping that could disable the alarm.
More questions: Branch Circuits, GFCI and AFCI
- 4049What is the minimum number of 20-ampere small-appliance branch circuits required for receptacle outlets in a dwelling kitchen, pantry, breakfast room and dining room?
- 4050Which of the following is permitted to be supplied by a dwelling small-appliance branch circuit?
- 4051How may the receptacle outlet for a dwelling kitchen refrigerator be supplied?
- 4052What branch circuit is required in a dwelling unit to supply the laundry receptacle outlets?
- 4053A single 20-ampere branch circuit supplies receptacle outlets in all three bathrooms of a house. What else may this circuit supply?
- 4054A 20-ampere branch circuit supplies only one bathroom of a dwelling. Which of the following may it also supply?