Branch-circuit wiring in a dwelling bedroom is extended by 4 ft to relocate a receptacle, with no new outlets or devices added. Is AFCI protection required for the extension?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4044
- D: No, extensions of 6 ft or less without added outlets are exempt
Explanation
210.12 requires AFCI protection when existing circuits in listed areas are modified, replaced or extended. An exception allows an extension of not more than 6 ft without any additional outlets or devices to remain without AFCI protection.