A 125-volt receptacle is installed on the roof of an office building for servicing a rooftop unit. What protection is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4018
- A: GFCI protection
Explanation
Rooftops are a listed location in 210.8(B) for other than dwelling units, so the receptacle needs GFCI protection. The servicing receptacle required near HVAC equipment by 210.63 is commonly in this location.