Under the NEC 2023 and 2026, a 125-volt receptacle installed behind the refrigerator in a dwelling kitchen does not serve the countertop and is more than 6 ft from the sink. Is GFCI protection required?

Exactly one answer is correct.

Show solution

Correct answer to question 4006

  • B: Yes, all receptacles in dwelling kitchens are covered

Explanation

Starting with the 2023 edition, the kitchen item in 210.8(A) applies to all receptacles in the kitchen, not only those serving the countertop. The refrigerator receptacle therefore needs GFCI protection.