Under NFPA 70E, when may an unqualified person cross the limited approach boundary?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 15007
- C: Only when advised of the hazards and continuously escorted by a qualified person
Explanation
NFPA 70E allows an unqualified person to cross the limited approach boundary only if a qualified person advises them of the hazards and continuously escorts them. They may never cross the restricted approach boundary.