Question 13121 of 790 · California General Electrician Exam

Three-phase 460 volt motors are rated 5 hp (7.6 A) and 3 hp (4.8 A). What is the minimum ampacity of a feeder supplying only these two motors?

Exactly one answer is correct.

Show solution

Correct answer to question 13121

  • A: 14.3 A

Explanation

125 % of the largest motor plus the other: 7.6 x 1.25 + 4.8 = 14.3 A. Applying 125 % to the smaller motor instead gives 13.6 A, and applying it to both gives 15.5 A.

Next to question ›