Question 13083 of 790 · California General Electrician Exam

A 25 hp, 460 volt, three-phase induction motor has a table full-load current of 34 A. What is the minimum ampacity of its branch-circuit conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 13083

  • C: 42.5 A

Explanation

Conductors for a single motor must have an ampacity of at least 125 % of the table full-load current: 34 x 1.25 = 42.5 A. Using 140 % (47.6 A) confuses this with overload limits.