Question 13061 of 790 · California General Electrician Exam
What adjustment factor applies when 25 current-carrying conductors are installed in a single raceway longer than 24 inches?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13061
- A: 45 %
Explanation
The adjustment table assigns 45 % to 21 through 30 current-carrying conductors. 50 % covers 10 to 20, 40 % covers 31 to 40, and 35 % applies to 41 and above.
More questions: Electrical Calculations
- 13062What ambient temperature correction factor applies to a 75 °C rated conductor at an ambient of 38 °C (tables based on 30 °C)?
- 13063A device box contains four 12 AWG insulated conductors, two 12 AWG equipment grounding conductors and one receptacle on a yoke. What minimum box volume is required?
- 13064A box has internal cable clamps, six 14 AWG insulated conductors, two 14 AWG equipment grounding conductors and a single-pole switch. What minimum volume does 314.16 require?
- 13065A box has a marked volume of 18.0 cubic inches and will contain only 12 AWG conductors with no fittings, devices or grounding conductors. What is the maximum number of conductors permitted?
- 13066A box contains four 12 AWG and two 14 AWG insulated conductors, 12 AWG equipment grounding conductors and a receptacle connected to the 12 AWG conductors. What minimum volume is required?
- 13067What is the volume listed in 314.16(A) for a 4 inch by 2-1/8 inch square metal box?