Question 13026 of 790 · California General Electrician Exam
A 4 ohm resistor is connected in series with a parallel group of 6 ohms and 12 ohms, and the circuit is supplied at 120 volts. What is the total current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13026
- B: 15 A
Explanation
The parallel group is (6 x 12) / (6 + 12) = 4 ohms, so the total is 4 + 4 = 8 ohms and I = 120 / 8 = 15 A. Treating all three as series (22 ohms) gives 5.45 A.
More questions: Electrical Calculations
- 13027Four identical 40 ohm heating elements are connected in parallel. What is the combined resistance?
- 13028Resistors of 5, 10 and 15 ohms are connected in series across 120 volts. What is the voltage across the 10 ohm resistor?
- 13031A 120 volt single-phase branch circuit uses 12 AWG copper (6,530 circular mils), runs 100 feet one way and carries 16 A. Using K = 12.9, what is the voltage drop?
- 13032A 240 volt single-phase circuit of 10 AWG copper (10,380 circular mils) supplies 24 A at 150 feet one way. What is the voltage drop as a percentage of the supply voltage?
- 13033A three-phase 480 volt load draws 50 A over 6 AWG copper conductors (26,240 circular mils), 200 feet one way. What is the line-to-line voltage drop?
- 13034A 240 volt single-phase feeder uses 4 AWG aluminum conductors (41,740 circular mils), 175 feet one way, carrying 60 A. Using K = 21.2 for aluminum, what is the voltage drop?