Question 12117 of 925 · California General Electrician Exam

Nine 5 kW electric dryers in a multifamily building are on one service. Using the NEC 2020 or 2023 dryer demand factors, what is the dryer load?

Exactly one answer is correct.

Show solution

Correct answer to question 12117

  • A: 24,750 VA

Explanation

9 x 5,000 VA = 45,000 VA. The demand factor for nine dryers is 55 % (Table 220.54), so the load is 24,750 VA.

Next to question ›