What is the minimum size of the bonding conductor for a communications primary protector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11040
- C: 14 AWG copper
Explanation
The primary protector bonding conductor must be copper or other corrosion-resistant conductive material not smaller than 14 AWG. It connects to the intersystem bonding termination or another approved point.