Where Class 2 conductors are not in a raceway, they must generally be separated from electric light and power conductors by at least what distance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11024
- C: 2 in
Explanation
Class 2 and Class 3 circuit conductors must be separated at least 2 in from power and Class 1 conductors unless an approved separation method is used. Approved alternatives include nonconductive sleeves or barriers between the circuits.