Correct answer to question 1102
- C: Utility-owned generation and distribution equipment under the utility's exclusive control
Explanation
90.2 lists installations under the exclusive control of an electric utility for generation, transmission and distribution as not covered by the Code. Premises wiring on the load side of the service point is covered.