Question 10023 of 1003 · California General Electrician Exam
A junction box connected to a conduit that extends directly to a wet-niche forming shell is mounted on the pool deck. Its top must be at least how high above the maximum water level?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10023
- D: 8 in
Explanation
The junction box must be located so its top is at least 4 in above the ground or deck and at least 8 in above the maximum pool water level, whichever gives the greater elevation. It must also be at least 4 ft from the inside wall unless separated by a fence or wall.
More questions: Special Equipment, Pools, PV and EV
- 10024A deck-mounted junction box for a wet-niche luminaire, not separated from the pool by a fence or wall, must be at least how far from the inside wall of the pool?
- 10025What is the minimum size of a solid copper equipotential bonding conductor for a permanently installed pool?
- 10027Perimeter surfaces around a pool must be bonded for what minimum horizontal distance beyond the inside walls?
- 10028When a copper grid is used for pool perimeter bonding, the conductors must form a grid with a uniform spacing of how much?
- 10029A copper ring or grid used for pool perimeter bonding is installed at what depth?
- 10030For conductive pool shells, perimeter surface bonding must attach to the structural reinforcing steel or copper grid at a minimum of how many points?